Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
|
|
#1 |
|
Member
Join Date: Jul 2008
Location: NE Indiana
Posts: 69
|
I bought a Hobart 220V welder and now need to install a plug & branch circuit. From what I can tell so far, I don't need 3 conductor wire. True? The manual claims 14 awg is Ok (see picture) but that seems light. What is recommended for a 30 amp breaker? I plan to install about 3 outlets in the garage on the same circuit, but I'll only weld on one at a time.
|
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 6,666
|
What model, I assume 187 or 210? Disregard the number 14/30 combination, that is the code minimum and the max breaker for that minimum wire. A 10 wire with 30 breaker makes tailor made circuit, 12 would be sufficient but personally I go the 10 and it makes allowances for some future machines. This machine can run on circuits to 50A, it actually comes with 50A plug. It needs a total of 3 wires, 2 conductors and a ground.
__________________
www.urkafarms.com |
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Jan 2006
Location: SW Florida
Posts: 781
|
I need to run some wiring in conduit, for a Welder plug that is about 50 - 60' from the panel. What size wires do I use, or would I try and pull some 6-3 through the conduit w/ alot of lube ?
|
|
|
|
|
|
#4 |
|
Senior Member
Join Date: Mar 2007
Location: The Gunshine state
Posts: 2,082
|
Run two copper #6 THHN and one copper #8 THHN.
__________________
http://www.ExquisitePlatingAndCoating.com |
|
|
|
|
|
#5 |
|
Senior Member
Join Date: Jan 2007
Location: Eastern Oregon
Posts: 1,601
|
I usually pull 8's and a 10 if I'm using THHN for the 50 amp welder circuits.
As a sidenote, I know welders can get away with smaller wire than is typically used, but I don't trust people enough to think it'll always be used for a welder. I know a week after I leave they'll plug a range into it or monster heater, large air compressor, etc and cook the wiring..... Which means they get full sized wire for the circuit ampacity at a slightly elevated expense. |
|
|
|
|
|
#6 |
|
Senior Member
Join Date: Jan 2006
Location: SW Florida
Posts: 781
|
Thanks...this will be for a 50 amp welder circuit, by the door, then i'll use a 25' cord to get further out on the apron if need be.
|
|
|
|
|
|
#7 |
|
Senior Member
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 6,666
|
I am with Ace here, 2-8's and a 10 and will serve most machines likely to be found in a home garage, up to 250A migs and all the simple transformer stick machines. Some of the 200A plus TIG machines have different requirements.
__________________
www.urkafarms.com |
|
|
|
|
|
#8 |
|
Senior Member
Join Date: Jan 2006
Location: SW Florida
Posts: 781
|
what size conduit would you recomend??
|
|
|
|
|
|
#9 |
|
Senior Member
Join Date: Nov 2007
Location: USA
Posts: 169
|
What did you end up deciding to pull?
|
|
|
|
|
|
#10 |
|
Senior Member
Join Date: Jan 2006
Location: SW Florida
Posts: 781
|
|
|
|
|
|
|
#11 |
|
Senior Member
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 6,666
|
8's and a 10 will go thru 3/4
__________________
www.urkafarms.com |
|
|
|
|
|
#12 |
|
Senior Member
Join Date: Jan 2006
Location: SW Florida
Posts: 781
|
thanks sberry27
|
|
|
|
|
|
#13 |
|
Member
Join Date: Jun 2007
Posts: 76
|
I am installing the same welder this week(Hobart handler 187). My outlet will be located directly under the garage subpanel(within 5 feet). Will 10 guage wire be suffecient and a 30 amp breaker. I am new to the whole 220 volt stuff but I am assuming that i hook two hots up to the breaker and a ground correct. Its the same as a regular outlet but ahs two wires isntead of one.
Another question si if home depot dont sell wire in small rolls(5 feet) and I ahve to puchase a 25 foot length. Would I be able to use the extra 10 guage wire to make an extention cord for the welder. If I only need 5 feet for the outlet can I use the extra 20 feet for an entension cord. Is 10 guage suffecient for this. Sorry for all the questions i am new to the electric game. Thanks Guys |
|
|
|
|
|
#14 |
|
Senior Member
Join Date: Apr 2008
Location: Cedar,BC
Posts: 1,029
|
#10 will do the job,but for a short distance like that,just use #8 for the extra buck or two it will cost.HD should be able to cut 8/3 NMD by the foot,just don't use the white conductor.NMD/NMW cable is not to be used as an extension cord,it is not that durable or flexible,and the cord ends don't always grip it properly.
|
|
|
|
|
|
#15 |
|
Senior Member
Join Date: Feb 2008
Location: Cumming, GA
Posts: 812
|
You can generally buy wire by the foot at HD or Lowes.
For an extension cord you want the flexible SO type cord. For the panel/receptacle wiring you want Romex. My 220V circuits are 10ga with 30a breakers.
__________________
'02 F350 PSD - tow pig '97 Jeep TJ offroad buggy '03 Rendezvous - for getting around '12 Chrysler 200 - wife's grocery getter |
|
|
|
|
|
#16 | |
|
Senior Member
Join Date: Dec 2008
Location: Northern Virginia
Posts: 636
|
Quote:
You need three conductors - two poles plus gnd. Pull 3 conductor 10 AWG from your 30 A bkr to your three 30A receptacles |
|
|
|
|
|
|