You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Sponsored Links (Register now to hide all advertisements)

Reply
 
Thread Tools Search this Thread Display Modes
Old 08-09-2011, 01:03 AM   #21
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 11,051
Default Re: Why do some breakers have two wire receiving slots?

THIS GE brochure offers no indication that their residential series breakers accommodate more than one wire per terminal, see p.14 (PDF file p. 15).

Charles
Charles (in GA) is offline   Reply With Quote
Old 08-09-2011, 01:21 AM   #22
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 11,051
Default Re: Why do some breakers have two wire receiving slots?

THIS Eaton/C-H document shows that 15 and 20 amp CH breakers are approved for one or two wires, and for BR breakers (formerly Bryant) there is no indication that they are allowed to accept two wires. See Data Tables 1-2 and 1-3 and 1-10 and 1-11.

Charles
Charles (in GA) is offline   Reply With Quote
Sponsored Links (Register now to hide all advertisements)
Old 08-09-2011, 10:15 AM   #23
Neuswede
Senior Member
 
Neuswede's Avatar
 
Join Date: Jul 2011
Location: Central Pennsylvania
Posts: 390
Default Re: Why do some breakers have two wire receiving slots?

Also looked at the service panel requirements:

Article 110-3(b) of the NEC states that Listed or labeled equipment shall be used or installed in accordance with any instructions included in the listing or labeling. Just because a breaker fits in the panel does not mean that it is okay to install it in that panel.

If a particular breaker is labeled as meeting a certain "classification", then it complies with this specification. When UL tests a particular breaker, they do so as to meeting a certain classification; not a particular manufacturer's specification.

All service panels contain the typical legal-eze: Only use Type XX or Brand XX breakers or you void the manufacturer's warranty... blah, blah, bladdy, blah, blah.

Also on the wire nuts, read section 312.8...about as clear as mud. It addresses the use of "gutter-area" in service panels. My pre-purchase home inspection found these used within the service panel and was an immediate failure. We also found enough other issues that we gutted the wiring and installed all new service panel and new circuits before moving in.

While NEC is a good starting point, each state and even localities can have differing interpretation of what should or shouldn't be permitted.

Just an FYI.
__________________


See my garage build at: http://www.garagejournal.com/forum/s...=1#post1620729
Neuswede is offline   Reply With Quote
Old 08-09-2011, 06:13 PM   #24
sdowney717
Senior Member
 
Join Date: Mar 2010
Posts: 918
Default Re: Why do some breakers have two wire receiving slots?

http://activerain.com/blogsview/1441...rcuit-breakers
http://www.nachi.org/forum/f19/doubl...reakers-28267/
I was flat out told NO to this by my electrical inspector.
Not sure why it came up when he did my inspection. I think it crossed my mind at the time you could do that.
But he threw cold water on the idea. Said just use a wire nut.
The above articles shows it ought to be ok if the breaker was made to do it.
sdowney717 is offline   Reply With Quote
Old 08-09-2011, 06:18 PM   #25
ishiboo
Senior Member
 
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 4,363
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by sdowney717 View Post
http://activerain.com/blogsview/1441...rcuit-breakers
http://www.nachi.org/forum/f19/doubl...reakers-28267/
I was flat out told NO to this by my electrical inspector.
Not sure why it came up when he did my inspection. I think it crossed my mind at the time you could do that.
But he threw cold water on the idea. Said just use a wire nut.
The above articles shows it ought to be ok if the breaker was made to do it.
Yup, just ignorance if you had a panel that supports it. I highly doubt any local code would override something like that, it's perfectly safe.
ishiboo is offline   Reply With Quote
Old 08-09-2011, 08:43 PM   #26
rabidsquirrel
Senior Member
 
rabidsquirrel's Avatar
 
Join Date: Jul 2010
Location: SE Pennsylvania
Posts: 283
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by Neuswede View Post
Also on the wire nuts, read section 312.8...about as clear as mud..
It's actually very clear. As long as you have sufficient wire fill, you can splice in a panel enclosure. Think of it as a large junction box. Failing a home inspection on that is asinine. The more I hear about home inspectors, the more I think they are a waste of money.
rabidsquirrel is offline   Reply With Quote
Old 08-10-2011, 12:05 AM   #27
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 11,051
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by rabidsquirrel View Post
It's actually very clear. As long as you have sufficient wire fill, you can splice in a panel enclosure. Think of it as a large junction box. Failing a home inspection on that is asinine. The more I hear about home inspectors, the more I think they are a waste of money.
And adding a splice or two, or even several, is not going to come close to the fill limits they specify. Its not uncommon to have splices in panels when you replaced a smaller, older panel with a new, large one. The wires never reach to the breaker, so you end up splicing them, or running a new wire back to the first junction, which is time consuming. You need to get that panel in and working right away, so you splice in the panel.

Charles
Charles (in GA) is offline   Reply With Quote
Old 08-10-2011, 09:55 AM   #28
Zeke
Senior Member
 
Zeke's Avatar
 
Join Date: Aug 2009
Location: Senior Member—in more ways than one.
Posts: 8,946
Default Re: Why do some breakers have two wire receiving slots?

No wire nuts in the breaker panel around here. When doing a service change out, a box is often placed next to the panel where all such connections are made.
Zeke is offline   Reply With Quote
Old 04-25-2012, 03:10 PM   #29
Fred Ming
Junior Member
 
Join Date: Apr 2012
Posts: 1
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by Zeke View Post
Nice answer. I have a couple or wiring books and these breakers are not mentioned.

Try to be a little more helpful and a little less snide.
I gotta say, that's how it felt when I read his post. Soldier on . . .
Fred Ming is offline   Reply With Quote
Old 04-26-2012, 07:39 AM   #30
hh76
Senior Member
 
hh76's Avatar
 
Join Date: Nov 2010
Location: NE Wisconsin
Posts: 991
Default Re: Why do some breakers have two wire receiving slots?

to the original question, two wires if fine if the breaker is designed for it, but beware that an inspector may need to see proof, so have paperwork ready.

When it comes to failing a home inspection because of wire nuts in a LC, almost every older home I've ever worked on would fail if that were true. When doing a service swap, some do mount a gutter, or box to make connections, but usually it is if they know they will have to make up a lot of spices.

As far as "get a book" answers, I do think they have a place. I don't think we should encourage some people to pursue electrical work without doing some homework, esspecially when they ask questions that show that they have absolutely no idea what is going on. For this post, I think it is a great question, and I definately don't think it warrents that type of attitude. I imagine that there are a lot of electricians out there who are unaware of the rules.
hh76 is offline   Reply With Quote
Old 05-01-2012, 09:09 PM   #31
z28dad
Senior Member
 
Join Date: Jul 2010
Location: VA
Posts: 172
Default Re: Why do some breakers have two wire receiving slots?

I dont guess I have ever seen one. When I read the post I was thinking about an af or gf.. Most of the stuff I have worked on is ch brand.
z28dad is offline   Reply With Quote
Old 05-01-2012, 09:59 PM   #32
54FordPanel
Senior Member
 
54FordPanel's Avatar
 
Join Date: Aug 2009
Location: Fort 54, Littleton, Co
Posts: 4,477
Default Re: Why do some breakers have two wire receiving slots?

I gotta say I've been impressed with MrMark's electrical knowledge in the past, so I'm learning something by him asking the question.
__________________
"The Audacity Of Bull$#*%"

My 82 Jeep Cherokee Restoration
54FordPanel is offline   Reply With Quote
Old 05-01-2012, 10:12 PM   #33
Fred43
Junior Member
 
Join Date: Apr 2012
Location: Bellingham, MA
Posts: 14
Default Re: Why do some breakers have two wire receiving slots?

Hey, I've been doing this for almost 50 years and there is always something to learn. Sometimes from those new to the trade as well as those that pass on their yeas of knowledge. Snobbery is fine for fun but not to poke fun at a serious question.

Yes QO Sq "D"'s are made for two wires. Westinghouse, Bryant, Cutler Hammer BR's are not designed for two except the breaker lug will accept two wires. Some inspectors will approve the practice if you twist the wires together and they are the sam AWG.

It is not illegal to splice wires in a panel if you do not use up more than 40% of the wireway.

Last edited by Fred43; 05-01-2012 at 10:21 PM.
Fred43 is offline   Reply With Quote
Old 05-01-2012, 10:19 PM   #34
Fred43
Junior Member
 
Join Date: Apr 2012
Location: Bellingham, MA
Posts: 14
Default Re: Why do some breakers have two wire receiving slots?

hh76,
Good points.
I used to make a lot of money going out to check on HOME INSPECTOR's claims of poor wiring and equipment that need to be replaced. About 75% of the claims were bogus. The home inspectors take a 10 hour course in the five major trades and consider themselves experts. I used to charge to write a report for the buyer or seller so they could take it to the passing. After the passing I might consider working in the home, if asked to, to defray thought of bias in the report.

Last edited by Fred43; 05-01-2012 at 10:22 PM.
Fred43 is offline   Reply With Quote
Old 05-02-2012, 12:26 PM   #35
Milton Shaw
Senior Member
 
Join Date: Feb 2011
Posts: 1,691
Default Re: Why do some breakers have two wire receiving slots?

Haven't seen it mentioned but don't GCFI breakers always have terminals for two wires, the black and the neutral. They also always have the pigtail for connecting to the neutral. Could this be what the original poster was asking about "terminals for two wires".
Milton Shaw is offline   Reply With Quote
Old 05-02-2012, 12:40 PM   #36
DYNA BILL
Banned
 
Join Date: Sep 2009
Location: Missouri
Posts: 4,104
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by Torque1st View Post
Get yourself a book on basic electrical wiring at the library or Box store.
Quote:
Originally Posted by Torque1st View Post
If you had ANY knowledge of basic household electricity you would not be asking such a question. And you would have known Ohm's Law and how to use it and not make dumb comments.

My avatar is a character from Beyond Thunderdome.

Mr Mark obviously IS a noob at electrical work.
There are no stupid questions, but there are stupid answers.
You, sir, gave stupid answers.
DYNA BILL is offline   Reply With Quote
Old 05-02-2012, 01:44 PM   #37
Torque1st
Senior Member
 
Torque1st's Avatar
 
Join Date: Sep 2008
Location: KC Metro, Kansas
Posts: 5,668
Default Re: Why do some breakers have two wire receiving slots?

Quote:
Originally Posted by DYNA BILL View Post
There are no stupid questions, but there are stupid answers.
You, sir, gave stupid answers.
Jesus, I had many old timers here compliment me on my answer to this OLD thread that some newbie with one post opened back up. My answer was appropriate for the knowledge level of the OP.

That idiotic 'truism' you quoted is one of the dumbest things I have ever heard. A palliative for the ignorant masses. One would have to be rock stupid to go around quoting it...
__________________
Faster, Better, Cheaper: Pick Two
The FairTax
Follow the Money. -72chevy
Yes, I am insensitive and yes, not politically correct, and yes, Im sure I offended someone,... -Busted_Knuckles (Me too, plus I am old, tired, and grumpy!)
Read "The Marching Morons" Here
"Works" <> Safe, Good, or Right
"You can't fix stupid." -Ron White

Last edited by Torque1st; 05-02-2012 at 01:47 PM.
Torque1st is offline   Reply With Quote
Old 05-03-2012, 08:31 AM   #38
DYNA BILL
Banned
 
Join Date: Sep 2009
Location: Missouri
Posts: 4,104
Default Re: Why do some breakers have two wire receiving slots?

Ironically, your signature says a lot about you.
DYNA BILL is offline   Reply With Quote
Old 05-03-2012, 04:12 PM   #39
Torque1st
Senior Member
 
Torque1st's Avatar
 
Join Date: Sep 2008
Location: KC Metro, Kansas
Posts: 5,668
Default Re: Why do some breakers have two wire receiving slots?

Thank you!
__________________
Faster, Better, Cheaper: Pick Two
The FairTax
Follow the Money. -72chevy
Yes, I am insensitive and yes, not politically correct, and yes, Im sure I offended someone,... -Busted_Knuckles (Me too, plus I am old, tired, and grumpy!)
Read "The Marching Morons" Here
"Works" <> Safe, Good, or Right
"You can't fix stupid." -Ron White
Torque1st is offline   Reply With Quote
Old 05-03-2012, 06:18 PM   #40
rburke65
Senior Member
 
rburke65's Avatar
 
Join Date: Nov 2007
Location: Canfield, Ohio
Posts: 2,667
Default Re: Why do some breakers have two wire receiving slots?

Ditto....not very helpful.
rburke65 is offline   Reply With Quote
Reply

Thread Tools Search this Thread
Search this Thread:

Advanced Search
Display Modes