What 20a backwired outlet

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
I need to buy 60 20a back wired outlets. I dont want back stabbed outlets but ones like back stabbed but the screws clamp the wire not a spring. What do you pros like. Also ive been told its not good to pull a load through the outlet. So i guess you wire it using more wire nuts so the device doesnt become a carrying part of the wire? Is this a true problem or just a wives tale? Thanks alot guys
 
To avoid these ads, REGISTER NOW!

PT Doc

Well-known member
Joined
Nov 12, 2010
Messages
3,197
Are you asking of wiring outlets is better in parallel than in series?

If yes, then yes. If the outlets are close to one another like all in one box. If they are far apart then you will obviously need lots of wire.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I need to buy 60 20a back wired outlets. I dont want back stabbed outlets but ones like back stabbed but the screws clamp the wire not a spring. What do you pros like. Also ive been told its not good to pull a load through the outlet. So i guess you wire it using more wire nuts so the device doesnt become a carrying part of the wire? Is this a true problem or just a wives tale? Thanks alot guys
Back wired receptacles are fine. I prefer spec-grade receptacles. All back-wired receptacles are spec-grade. I do like side wired better, but back wired are just as good.
Wiring them through the side screws is FINE. Some will say that this is not good, but ALL devices like this ARE rated for feed-thru.

May I ask why 20A?
 
OP
C

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
I dont have a reason for 20a circuits other than bigger is better right. I ran my lighting off a 20a circuit and had a good amount of 12-2with ground left over. So i ran with it I guess. Also i have some large hand tools that i would like to use w/o worry. Thanks for the replies.
 

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
I dont have a reason for 20a circuits other than bigger is better right. I ran my lighting off a 20a circuit and had a good amount of 12-2with ground left over. So i ran with it I guess. Also i have some large hand tools that i would like to use w/o worry. Thanks for the replies.
I was asking why 20A receptacles.
20A circuits is fine (although I rarely do this for lighting circuits).
 
OP
C

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
Maybe im wrong but wouldn't i need a 20a outlet on a 20a circuit? The way my lighting fixtures are set up im 1 fixture over a 15a circuit capacity. They are flush mounted t-8s in a continuous row.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,109
Location
Minneapolis
You don't need 20 amp receptacles - as long as there are two or more receptacles on a 20 amp circuit (and a standard duplex receptacle counts as two) you're allowed to use 15 amp receptacles. And, most if not all 15 amp receptacles are rated for 20 amp feedthrough.

Most people don't have plug in devices that require anything more than a 15 amp receptacle anyway.
 

ForceFed70

Well-known member
Joined
Apr 27, 2010
Messages
3,441
Location
BC, Canada
In my neck of the woods, feed-thru is not allowed. You must pigtail. It's one of the 1st things the inspector looks at as part of your rough-in inspection.

I'm thinking there must be a reason why they've adapted this rule, but damned if I could tell you what it is.
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
You don't need 20 amp receptacles - as long as there are two or more receptacles on a 20 amp circuit (and a standard duplex receptacle counts as two) you're allowed to use 15 amp receptacles. And, most if not all 15 amp receptacles are rated for 20 amp feedthrough.


Then why do they even make 20A receptacles?


If you have a 20A circuit, why not use a 20A receptacle? There's very little difference in cost and you can tell at a glance that it's a 20A circuit.
 

rlitman

Well-known member
Joined
Oct 18, 2010
Messages
24,599
Location
Long Island
Then why do they even make 20A receptacles?


If you have a 20A circuit, why not use a 20A receptacle? There's very little difference in cost and you can tell at a glance that it's a 20A circuit.

There is a big difference in cost, if you are comparing spec grade outlets with the cheap ones. There is little difference in cost between spec grade 15 and 20A.

If you can find it, Hubbell makes the best outlets I've ever used.
 

theoldwizard1

Well-known member
Joined
Feb 22, 2011
Messages
43,155
Location
SE MI
In my neck of the woods, feed-thru is not allowed. You must pigtail. It's one of the 1st things the inspector looks at as part of your rough-in inspection.

I'm thinking there must be a reason why they've adapted this rule, but damned if I could tell you what it is.

Another one of those "Why did the change common practice ?" things. Like taking lead out of plumbing solder.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,109
Location
Minneapolis
Then why do they even make 20A receptacles?


If you have a 20A circuit, why not use a 20A receptacle? There's very little difference in cost and you can tell at a glance that it's a 20A circuit.

A 20 amp plug has one of the prongs turned sideways. Look at this picture of a 20 amp receptacle and you can see the one slot has a T shape so it can accept either a 15 amp or a 20 amp receptacle.

LEV_16342-W.jpg


If 20 amp receptacles are readily available and you can get them for little difference in cost, there's no problem in using them on a 20 amp circuit, but most people will never have a power tool that requires one.
 

FakeName

Well-known member
Joined
Nov 10, 2008
Messages
171
Location
San Diego, CA
So- do we still run 20 amp circuits?

I understand something like a compressor will want a dedicated 20 amp circuit, but for the several outlets we install along each garage wall- 15 or 20 amp?
 

Norcal

Well-known member
Joined
Mar 16, 2008
Messages
13,754
15A receptacles are rated 20A feed through, unless someone gets a good deal on 20A there is no reason to use them, unless you have extra money to squander.
 

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,109
Location
Minneapolis
Running 20 amp receptacle circuits can still be a good idea, if for instance you have several things plugged into the same circuit you can avoid nuisance trips.
 
To avoid these ads, REGISTER NOW!

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
I have at least 15, maybe 20 circuits in my shop that are 120 volt, 20A breakers, 12 gauge wire and 20A receptacles. Unless you're really pinching pennies, use 20A.

It gives you good flexibility for moving things around if you use space heaters, big power tools or maybe a 120V welder. If you'll never use that kind of equipment, then you don't need 20A circuits.

jmo
 

djjsr

Well-known member
Joined
Sep 4, 2006
Messages
4,796
Location
In the cornfields
15A receptacles are rated 20A feed through, unless someone gets a good deal on 20A there is no reason to use them, unless you have extra money to squander.


Ok, I think it's wrong, so once again I'll ask.

If 15A receptacles will do everything a 20A receptacle will do, then why do they bother selling 20A receptacles?

I have a space heater that's 120V and it has a 20A plug that will not plug into a 15A outlet.

There's a reason these exist ..........

403522774.jpg
 
Last edited:

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,109
Location
Minneapolis
I have a space heater that's 120V and it has a 20A plug that will not plug into a 15A outlet.

Well, that's one example of where you need a 20 amp receptacle, but appliances like that aren't very common.

As mentioned, the vast majority of 120vac consumer devices use a 15 amp plug, so they only need a 15 amp receptacle. Putting those 15 amp receptacles on a 20 amp circuit provides a little more capacity, if there are several devices plugged into the same circuit, and helps avoid having nuisance trips.

20 amp circuits aren't necessary by any means, but in a place like a garage or workshop where people are more likely to be using power tools that need more amps they're not a bad idea.
 

FakeName

Well-known member
Joined
Nov 10, 2008
Messages
171
Location
San Diego, CA
Thanks for all the info here- much appreciated.

So- is it a good idea to run 20 amp receptacle circuits with one 20amp outlet and the rest 15? This would allow the occasional 20 amp device and one could be sure to unplug anything else on that circuit for the duration of the 20 amp device's use?
 
OP
C

cyamaha2007

Well-known member
Joined
Apr 20, 2009
Messages
2,001
Location
St.Charles MO
As far as my lighting goes i will have 35 8ft t8 fixtures for 2000sqft. 14 will be on each circuit. Each fixture has a .98a draw. As far as a 20a outlets go my portable plasma, mag drill,spot welder, belt sander, hydraulic accessory pack have a 20a male plug so im stuck with using 20 a receptacles i guess. Thanks for the info. I had no idea you could use a 15a outlet on a 20a circuit. One more question can you use a 15a switch for a 20a circuit? Or is that a no no. My electrical training was 2 years trade school. So im no pro thats for sure.
 

soj

Well-known member
Joined
Dec 3, 2007
Messages
729
Location
North Georgia
One more reason for 20A rec. is a 10G extension cord. I have one with a 20A male plug, so with 20A rec. I can use it anywhere, esp on the outside rec. which is where I usually use the 100' 10G cord anyway.
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI
Ok, I think it's wrong, so once again I'll ask.

If 15A receptacles will do everything a 20A receptacle will do, then why do they bother selling 20A receptacles?

Originally, they were designed so that you wouldn't accidentally plug a 20a device into a 15a circuit, which best case scenario would blow the breaker/fuse/etc. In addition, back when there were fuses, if people kept blowing a fuse many would just put a bigger fuse in instead - bad idea! In addition, a breaker will pass overcurrent for a period of time. It also prevents you from putting a 20a space heater on a 100' 16-gauge extension cord, since no <12ga extension cord would have that plug.

For the shop, it's good to wire with #12 and breaker for 20a as you often run larger tools which often consume the power. A few devices also require 20a still - 120v welders at full output, for example.

I've never owned a piece of equipment with a 20amp plug, but when I wire a 20a receptacle circuit I almost always use 20a receptacles. Reason being, it is much easier to not accidentally buy the lowest-quality receptacles at the stores when you go up to 20a... and the price difference is slim to none between the two. 20a gets you a quality back-wired screw receptacle.

IEC connectors (the plugs that computer power supplies, LCD/Plasma TVs, etc. typically use) also come in 15a and 20a variants which are very different, and a 15a plug cannot go into a 20a receptacle. What sucked though is that they are used for both 120v and 240v in US datacenters, so power supplies which are not auto-switching go up in smoke if you accidentally plug one in to 240v with the switch set to 120. Ask me how I know :)
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Does the NEC require or recommend that a 20A receptacle be used on a 20A circuit?

20 amp receptacle is required if there is only one receptacle, that means a single receptacle, on the circuit. If there is a duplex receptacle, or more than one in any way, then 15 amp receptacles are OK.

NEC 210.21

(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.

(2) Total Cord-and-Plug-Connected Load. Where connected
to a branch circuit supplying two or more receptacles
or outlets, a receptacle shall not supply a total cord-and-plugconnected
load in excess of the maximum specified in Table
210.21(B)(2).

(3) Receptacle Ratings. Where connected to a branch circuit
supplying two or more receptacles or outlets, receptacle
ratings shall conform to the values listed in Table
210.21(B)(3), or, where rated higher than 50 amperes, the
receptacle rating shall not be less than the branch-circuit
rating.

Table 210.21(B)(2) Maximum Cord-and-Plug-Connected
Load to Receptacle
Circuit Rating (Amperes) - Receptacle Rating (Amperes) - Maximum Load (Amperes)
15 or 20 - 15 - 12
20 - 20 - 16
30 - 30 - 24
 

automobiliben

Well-known member
Joined
Jan 9, 2012
Messages
181
Location
Greenville, SC
Well I learned something tonight! Guess I will go and return those 20A outlets that I bought.

The cost difference is pretty significant, like 3Xs the price for the bulk boxes...
 

automobiliben

Well-known member
Joined
Jan 9, 2012
Messages
181
Location
Greenville, SC

Speedy Petey

Well-known member
Joined
Apr 22, 2012
Messages
1,430
Location
NY State
Which ones would you recommend?

Just an aside, my last shop was wired with the El cheapo ones and I never had an issue. But I don't mind spending a bit more to get a better outlet.

This is what I bought:

http://www.lowes.com/pd_61241-334-B... Duplex Electrical Outlet&CAWELAID=1368030917

IIRC, they didn't have any mid grade 15A receptacles.
I just ask for CR15's at the supply house.

Most manufacturers use this designation: https://www.google.com/search?q=cr1...cp.r_qf.&fp=5f6f9e525258df09&biw=1680&bih=912
 

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
In my neck of the woods, feed-thru is not allowed. You must pigtail. It's one of the 1st things the inspector looks at as part of your rough-in inspection.

I'm thinking there must be a reason why they've adapted this rule, but damned if I could tell you what it is.

I just want to make sure I follow this right because I always did it the way it is done in the second pic.

So if I understand correctly, the first pic is the way it should be done and the second pic is not recommended???


FH01NOV_OUTLET_04.jpg



bad_electrical_connections.gif
 

ishiboo

Well-known member
Joined
Oct 27, 2010
Messages
9,481
Location
Oshkosh, WI

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
There are tens of thousands of housed wired like that in the second pic. I'm not a real fan of it, because of the hassle of installation, you are trying to hook up four wires at once and its much stiffer to push back into the box (even after forming a Z in the wires). The pigtails mean much less effort to push back into the box, easier to replace in the future, but a little more box fill.

Charles
 

green.bubbly

Well-known member
Joined
Dec 14, 2008
Messages
2,156
Location
Lafayette, LA
Thanks Charles. I am thinking that with #12 wire, using the pigtail would be easier. Is there any thing code wise wrong with doing it the way shown in the second pic? Is that what forcedfed referred to as feed through?
 

sberry

Banned
Joined
Jun 18, 2005
Messages
35,747
Location
Brethren, Michigan
Even a 120V welder has a 15A plug, about the only place I can remember running across any 20A was floor cleaning equipment. I got to agree with Norcal, that was simple,,, you don't need it. I cant think of a single thing I own that has a 20A plug.
 