You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Reply
 
Thread Tools Display Modes
Old 07-30-2012, 09:06 AM   #21
djjsr
Senior Member
 
djjsr's Avatar
 
Join Date: Sep 2006
Location: In the cornfields
Posts: 2,859
Default Re: What 20a backwired outlet

I have at least 15, maybe 20 circuits in my shop that are 120 volt, 20A breakers, 12 gauge wire and 20A receptacles. Unless you're really pinching pennies, use 20A.

It gives you good flexibility for moving things around if you use space heaters, big power tools or maybe a 120V welder. If you'll never use that kind of equipment, then you don't need 20A circuits.

jmo
__________________
Don in Illinois, home of political corruption and government incompetence.
djjsr is offline   Reply With Quote
Old 07-30-2012, 09:15 AM   #22
djjsr
Senior Member
 
djjsr's Avatar
 
Join Date: Sep 2006
Location: In the cornfields
Posts: 2,859
Default Re: What 20a backwired outlet

Quote:
Originally Posted by Norcal View Post
15A receptacles are rated 20A feed through, unless someone gets a good deal on 20A there is no reason to use them, unless you have extra money to squander.

Ok, I think it's wrong, so once again I'll ask.

If 15A receptacles will do everything a 20A receptacle will do, then why do they bother selling 20A receptacles?

I have a space heater that's 120V and it has a 20A plug that will not plug into a 15A outlet.

There's a reason these exist ..........

__________________
Don in Illinois, home of political corruption and government incompetence.

Last edited by djjsr; 07-30-2012 at 09:21 AM.
djjsr is offline   Reply With Quote
Old 07-30-2012, 09:23 AM   #23
Stuart in MN
Senior Member
 
Stuart in MN's Avatar
 
Join Date: Sep 2005
Location: Minneapolis
Posts: 6,545
Default Re: What 20a backwired outlet

Quote:
Originally Posted by djjsr View Post
I have a space heater that's 120V and it has a 20A plug that will not plug into a 15A outlet.
Well, that's one example of where you need a 20 amp receptacle, but appliances like that aren't very common.

As mentioned, the vast majority of 120vac consumer devices use a 15 amp plug, so they only need a 15 amp receptacle. Putting those 15 amp receptacles on a 20 amp circuit provides a little more capacity, if there are several devices plugged into the same circuit, and helps avoid having nuisance trips.

20 amp circuits aren't necessary by any means, but in a place like a garage or workshop where people are more likely to be using power tools that need more amps they're not a bad idea.
Stuart in MN is offline   Reply With Quote
Old 07-30-2012, 11:41 AM   #24
FakeName
Senior Member
 
FakeName's Avatar
 
Join Date: Nov 2008
Location: San Diego, CA
Posts: 169
Default Re: What 20a backwired outlet

Thanks for all the info here- much appreciated.

So- is it a good idea to run 20 amp receptacle circuits with one 20amp outlet and the rest 15? This would allow the occasional 20 amp device and one could be sure to unplug anything else on that circuit for the duration of the 20 amp device's use?
FakeName is offline   Reply With Quote
Old 07-30-2012, 05:34 PM   #25
cyamaha2007
Senior Member
 
cyamaha2007's Avatar
 
Join Date: Apr 2009
Location: St.Charles MO
Posts: 1,765
Default Re: What 20a backwired outlet

As far as my lighting goes i will have 35 8ft t8 fixtures for 2000sqft. 14 will be on each circuit. Each fixture has a .98a draw. As far as a 20a outlets go my portable plasma, mag drill,spot welder, belt sander, hydraulic accessory pack have a 20a male plug so im stuck with using 20 a receptacles i guess. Thanks for the info. I had no idea you could use a 15a outlet on a 20a circuit. One more question can you use a 15a switch for a 20a circuit? Or is that a no no. My electrical training was 2 years trade school. So im no pro thats for sure.
__________________
Check out my 36wx56Lx14h pole barn build done the hard way http://www.garagejournal.com/forum/s...d.php?t=118655
cyamaha2007 is offline   Reply With Quote
Old 07-30-2012, 09:19 PM   #26
soj
Member
 
Join Date: Dec 2007
Location: Central Ar
Posts: 81
Default Re: What 20a backwired outlet

One more reason for 20A rec. is a 10G extension cord. I have one with a 20A male plug, so with 20A rec. I can use it anywhere, esp on the outside rec. which is where I usually use the 100' 10G cord anyway.
soj is offline   Reply With Quote
Old 07-30-2012, 09:50 PM   #27
ishiboo
Senior Member
 
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
Default Re: What 20a backwired outlet

Quote:
Originally Posted by djjsr View Post
Ok, I think it's wrong, so once again I'll ask.

If 15A receptacles will do everything a 20A receptacle will do, then why do they bother selling 20A receptacles?
Originally, they were designed so that you wouldn't accidentally plug a 20a device into a 15a circuit, which best case scenario would blow the breaker/fuse/etc. In addition, back when there were fuses, if people kept blowing a fuse many would just put a bigger fuse in instead - bad idea! In addition, a breaker will pass overcurrent for a period of time. It also prevents you from putting a 20a space heater on a 100' 16-gauge extension cord, since no <12ga extension cord would have that plug.

For the shop, it's good to wire with #12 and breaker for 20a as you often run larger tools which often consume the power. A few devices also require 20a still - 120v welders at full output, for example.

I've never owned a piece of equipment with a 20amp plug, but when I wire a 20a receptacle circuit I almost always use 20a receptacles. Reason being, it is much easier to not accidentally buy the lowest-quality receptacles at the stores when you go up to 20a... and the price difference is slim to none between the two. 20a gets you a quality back-wired screw receptacle.

IEC connectors (the plugs that computer power supplies, LCD/Plasma TVs, etc. typically use) also come in 15a and 20a variants which are very different, and a 15a plug cannot go into a 20a receptacle. What sucked though is that they are used for both 120v and 240v in US datacenters, so power supplies which are not auto-switching go up in smoke if you accidentally plug one in to 240v with the switch set to 120. Ask me how I know
ishiboo is offline   Reply With Quote
Old 07-31-2012, 06:42 AM   #28
djjsr
Senior Member
 
djjsr's Avatar
 
Join Date: Sep 2006
Location: In the cornfields
Posts: 2,859
Default Re: What 20a backwired outlet

Does the NEC require or recommend that a 20A receptacle be used on a 20A circuit?
__________________
Don in Illinois, home of political corruption and government incompetence.
djjsr is offline   Reply With Quote
Old 07-31-2012, 07:23 AM   #29
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,837
Default Re: What 20a backwired outlet

Quote:
Originally Posted by djjsr View Post
Does the NEC require or recommend that a 20A receptacle be used on a 20A circuit?
20 amp receptacle is required if there is only one receptacle, that means a single receptacle, on the circuit. If there is a duplex receptacle, or more than one in any way, then 15 amp receptacles are OK.

Quote:
NEC 210.21

(B) Receptacles.
(1) Single Receptacle on an Individual Branch Circuit.
A single receptacle installed on an individual branch circuit
shall have an ampere rating not less than that of the branch
circuit.

(2) Total Cord-and-Plug-Connected Load. Where connected
to a branch circuit supplying two or more receptacles
or outlets, a receptacle shall not supply a total cord-and-plugconnected
load in excess of the maximum specified in Table
210.21(B)(2).

(3) Receptacle Ratings. Where connected to a branch circuit
supplying two or more receptacles or outlets, receptacle
ratings shall conform to the values listed in Table
210.21(B)(3), or, where rated higher than 50 amperes, the
receptacle rating shall not be less than the branch-circuit
rating.

Table 210.21(B)(2) Maximum Cord-and-Plug-Connected
Load to Receptacle
Circuit Rating (Amperes) - Receptacle Rating (Amperes) - Maximum Load (Amperes)
15 or 20 - 15 - 12
20 - 20 - 16
30 - 30 - 24
Charles (in GA) is offline   Reply With Quote
Old 07-31-2012, 10:10 AM   #30
djjsr
Senior Member
 
djjsr's Avatar
 
Join Date: Sep 2006
Location: In the cornfields
Posts: 2,859
Default Re: What 20a backwired outlet

Thanks Charles.
__________________
Don in Illinois, home of political corruption and government incompetence.
djjsr is offline   Reply With Quote
Old 08-03-2012, 10:53 PM   #31
automobiliben
Senior Member
 
automobiliben's Avatar
 
Join Date: Jan 2012
Location: Greenville, SC
Posts: 160
Default Re: What 20a backwired outlet

Well I learned something tonight! Guess I will go and return those 20A outlets that I bought.

The cost difference is pretty significant, like 3Xs the price for the bulk boxes...
automobiliben is offline   Reply With Quote
Old 08-04-2012, 07:52 AM   #32
Speedy Petey
Senior Member
 
Join Date: Apr 2012
Location: NY State
Posts: 651
Default Re: What 20a backwired outlet

Quote:
Originally Posted by automobiliben View Post

The cost difference is pretty significant, like 3Xs the price for the bulk boxes...
Make sure you still get spec-grade receptacles. The cheap <$1 ones are not worth it.
Speedy Petey is offline   Reply With Quote
Old 08-04-2012, 07:59 AM   #33
automobiliben
Senior Member
 
automobiliben's Avatar
 
Join Date: Jan 2012
Location: Greenville, SC
Posts: 160
Default Re: What 20a backwired outlet

Quote:
Originally Posted by Speedy Petey View Post
Make sure you still get spec-grade receptacles. The cheap <$1 ones are not worth it.
Which ones would you recommend?

Just an aside, my last shop was wired with the El cheapo ones and I never had an issue. But I don't mind spending a bit more to get a better outlet.

This is what I bought:

http://www.lowes.com/pd_61241-334-BR...AID=1368030917

IIRC, they didn't have any mid grade 15A receptacles.
automobiliben is offline   Reply With Quote
Old 08-04-2012, 10:11 AM   #34
Speedy Petey
Senior Member
 
Join Date: Apr 2012
Location: NY State
Posts: 651
Default Re: What 20a backwired outlet

Quote:
Originally Posted by automobiliben View Post
Which ones would you recommend?

Just an aside, my last shop was wired with the El cheapo ones and I never had an issue. But I don't mind spending a bit more to get a better outlet.

This is what I bought:

http://www.lowes.com/pd_61241-334-BR...AID=1368030917

IIRC, they didn't have any mid grade 15A receptacles.
I just ask for CR15's at the supply house.

Most manufacturers use this designation: https://www.google.com/search?q=cr15...w=1680&bih=912
Speedy Petey is offline   Reply With Quote
Old 08-04-2012, 07:37 PM   #35
automobiliben
Senior Member
 
automobiliben's Avatar
 
Join Date: Jan 2012
Location: Greenville, SC
Posts: 160
Default Re: What 20a backwired outlet

Quote:
Originally Posted by Speedy Petey View Post
I just ask for CR15's at the supply house.

Most manufacturers use this designation: https://www.google.com/search?q=cr15...w=1680&bih=912
I returned what I had bought and picked some of these up. They are $16 for a box of 10 at Home Depot.
automobiliben is offline   Reply With Quote
Old 08-05-2012, 05:42 PM   #36
green.bubbly
Senior Member
 
green.bubbly's Avatar
 
Join Date: Dec 2008
Location: Lafayette, LA
Posts: 1,409
Default Re: What 20a backwired outlet

Quote:
Originally Posted by ForceFed70 View Post
In my neck of the woods, feed-thru is not allowed. You must pigtail. It's one of the 1st things the inspector looks at as part of your rough-in inspection.

I'm thinking there must be a reason why they've adapted this rule, but damned if I could tell you what it is.
I just want to make sure I follow this right because I always did it the way it is done in the second pic.

So if I understand correctly, the first pic is the way it should be done and the second pic is not recommended???





__________________
.
.
.
.
.

_______________________________________

My garage and steel home build thread...
http://garagejournal.com/forum/showthread.php?t=91518
green.bubbly is offline   Reply With Quote
Old 08-05-2012, 05:53 PM   #37
ishiboo
Senior Member
 
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,326
Default Re: What 20a backwired outlet

Quote:
Originally Posted by automobiliben View Post
Which ones would you recommend?

Just an aside, my last shop was wired with the El cheapo ones and I never had an issue. But I don't mind spending a bit more to get a better outlet.

This is what I bought:

http://www.lowes.com/pd_61241-334-BR...AID=1368030917

IIRC, they didn't have any mid grade 15A receptacles.
Those are acceptable... that's what I use. You're usually safe with any of the backwire receptacles.
ishiboo is offline   Reply With Quote
Old 08-05-2012, 06:58 PM   #38
Charles (in GA)
Senior Member
 
Charles (in GA)'s Avatar
 
Join Date: Jan 2006
Location: 50 mi south of Atlanta
Posts: 8,837
Default Re: What 20a backwired outlet

There are tens of thousands of housed wired like that in the second pic. I'm not a real fan of it, because of the hassle of installation, you are trying to hook up four wires at once and its much stiffer to push back into the box (even after forming a Z in the wires). The pigtails mean much less effort to push back into the box, easier to replace in the future, but a little more box fill.

Charles
Charles (in GA) is offline   Reply With Quote
Old 08-05-2012, 07:08 PM   #39
green.bubbly
Senior Member
 
green.bubbly's Avatar
 
Join Date: Dec 2008
Location: Lafayette, LA
Posts: 1,409
Default Re: What 20a backwired outlet

Thanks Charles. I am thinking that with #12 wire, using the pigtail would be easier. Is there any thing code wise wrong with doing it the way shown in the second pic? Is that what forcedfed referred to as feed through?
__________________
.
.
.
.
.

_______________________________________

My garage and steel home build thread...
http://garagejournal.com/forum/showthread.php?t=91518
green.bubbly is offline   Reply With Quote
Old 08-05-2012, 11:43 PM   #40
sberry
Senior Member
 
sberry's Avatar
 
Join Date: Jun 2005
Location: Brethren, Michigan
Posts: 6,706
Default Re: What 20a backwired outlet

Even a 120V welder has a 15A plug, about the only place I can remember running across any 20A was floor cleaning equipment. I got to agree with Norcal, that was simple,,, you don't need it. I cant think of a single thing I own that has a 20A plug.
__________________
www.urkafarms.com
sberry is offline   Reply With Quote
Reply

Thread Tools
Display Modes

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off

Forum Jump


All times are GMT -5. The time now is 01:26 AM.