What control would use the floor temperature as input? Just curious.
Ken
There are a couple out there that regulate slab temp or use it in conjunction with the room air temp and outside air temp to predict the needed run time of the heater.
These stats are expensive and in general folks are very happy with just an air temp stat.
I just imagine monitoring room temp is fine until the overhead doors are open and the air temp drops 30 degrees in the room. The air temp stat kicks on the boiler, the doors are shut, and before the running boiler has any impact on air temp the slab is able to reheat the room air and the air temp stat shuts the boiler off. Seems to be a waste.
Since slab temp takes many hours to change and air temp changes in seconds there will be some lag.
So bottom line is adding a scrap piece of pex in the pour as a slab temp sensor sleeve is easy and cheap. Only get one chance and you may want to monitor it for thrills.