2-2-2-4 Mobile Home Feeder wire for Garage?

ebasista

Well-known member
Joined
Dec 25, 2008
Messages
56
I decided to go with Mobile home feeder wire for my subpanel in the garage. Its going to be 2-2-2-4 AL wire, breakered in the main panel at 90A connected to a 100A main disconnect subpanel in the garage.

http://www.southwire.com/ProductCatalog/XTEInterfaceServlet?contentKey=prodcatsheet15

I understand that I can direct bury this wire, and will use sch80 to go from the ground to the house and garage.

What do I have to do inside the house with this wire to protect it....is conduit required in the house for this, or can i run it thru the crawlspace to the panel without any additional shielding?
 
To avoid these ads, REGISTER NOW!

mrb

Well-known member
Joined
Dec 31, 2008
Messages
3,734
make sure the cable you get has the RHH / RHW listing or it cant enter the structure. It would need to be in conduit inside the house since its individual wires and not a jacketed cable.

I wouldnt use the stuff. I would go conduit all the way and individual AL conductors.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
make sure the cable you get has the RHH / RHW listing or it cant enter the structure. It would need to be in conduit inside the house since its individual wires and not a jacketed cable.

I wouldnt use the stuff. I would go conduit all the way and individual AL conductors.

I have 150 ft of this same cable. I think the brochure he linked to says it all.

Southwire mobile home feeder consists of four quadruplexed type RHH or RHW-2 or USE-2 AlumaFlex TM AA-8000 series
aluminum alloy compacted conductors. The cable contains a triple extruded white striped neutral conductor and a green
grounding conductor to eliminate the need for field marking per the National Electrical Code. Insulation is sunlight resistant .


Indeed, the cable, consisting of four individual wires twisted together are marked with all the specs indicated in the brochure.

Charles
 

bward76

Active member
Joined
Jan 19, 2009
Messages
25
I agree to using conduit as well but If you insist on direct burial be very very certain that it is in a path that will never be near any trees or bushes. I had a service account a few years back that fed hundreds of mobile homes (built about 20 years ago) all in direct burial cable. Over the coarse of a couple years, I replaced probably 30 sets of their feeders that had been destroyed by roots over time. This involved trenching from the transformer to the unit on every one(very expensive). In this case a lot of t.v.'s and appliances were damaged when the problems occurred.
 
To avoid these ads, REGISTER NOW!
OP
E

ebasista

Well-known member
Joined
Dec 25, 2008
Messages
56
There will never be tree roots or shrubs to worry about in this location (too close to my house and never plan on putting stuff there).

Inside the house I take it I'm required to use conduit in the crawlspace up to the box (whats the minimum size for that)? I would like to avoid using conduit in the house because of the hassle, can I connect this to shielded cable inside the house?
 

Iseman

Well-known member
Joined
Dec 5, 2008
Messages
48
Location
Kerrville, TX
I used the same wire and direct buried it like the manufacture approves. BIG BIG BIG mistake. Even with no trees or bushs nearby it can still come in contact with moisture or water. When I put in the new line 2 years later, the electrician said it happens all the time. There is a nick or crack in the insulation and now you have burn thru. Bury it in a conduit, be safe and not sorry. Cost me an additional $3000 to fix. Conduit less than $200. Just my oppinion. Maybe to late.
 

bimmer1980

Well-known member
Joined
Feb 5, 2009
Messages
2,104
Location
York, PA
2" PVC really isn't all that hard to run..... I just finished running some 2" PVC from my garage to the house (including under a driveway) and pulling 2# copper... not bad at all....
 