You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today!

If you have any problems with the registration process or your account login, please contact contact us.

Go Back   The Garage Journal Board > The Garage > Lighting & Electrical

Reply
 
Thread Tools Display Modes
Old 07-19-2012, 07:53 PM   #41
eljefino
Senior Member
 
Join Date: Feb 2008
Posts: 261
Default Re: Adding a New Garage Circuit

Well... I heard the opposite, that "skin effect" favors stranded wire. But it's not that big a deal at 60Hz.

OTOH, when you put an extension cord on an outlet, you've added more length of wire, and another connection, both of which are slightly detrimental.

I've run my air compressor (regular cheapie 1.5 hp) on a 16 gauge extension cord and it was not happy at all, slow to start, smelling hot. Put it on the 12 ga yellow jacket and it purred like it was plugged into the wall.

I would absolutely wire for 20 amp/ 12 ga. It'll keep the lights from dimming as badly when you start up a tool.
eljefino is offline   Reply With Quote
Old 07-23-2012, 11:02 AM   #42
Ferrino
Senior Member
 
Join Date: Mar 2011
Posts: 131
Default Re: Adding a New Garage Circuit

Quote:
Originally Posted by pattenp View Post
It's okay by NEC to use 15A receptacles on a 20A circuit. There's no need to buy the actual 20A receptacles that have the T shaped slot on one side.
Why is this the case? Is it because a device that has the 15A 3-pin plug will never draw more than 15A and will therefore never exceed the rated limit of the 15A outlet?

In that case, the only advantage of having a 20A circuit over a 15A circuit is when you have multiple devices running, yes?
Ferrino is offline   Reply With Quote
Old 07-23-2012, 11:05 AM   #43
Alchymist
Senior Member
 
Alchymist's Avatar
 
Join Date: Mar 2009
Location: Central PA
Posts: 2,441
Default Re: Adding a New Garage Circuit

Quote:
Originally Posted by Ferrino View Post
Why is this the case? Is it because a device that has the 15A 3-pin plug will never draw more than 15A and will therefore never exceed the rated limit of the 15A outlet?

In that case, the only advantage of having a 20A circuit over a 15A circuit is when you have multiple devices running, yes?
The other advantage of the 20 amp circuit is for motor starting- power tools that don't draw more than 15 amps sometimes have a much higher starting current. (Think circular saw, table saw, etc).
Alchymist is offline   Reply With Quote
Old 07-23-2012, 11:39 AM   #44
FluxCore
Senior Member
 
Join Date: May 2012
Location: Born and raised in Germany, settled in Lousyana
Posts: 229
Default Re: Adding a New Garage Circuit

Gooberheads, we select 20A outlets and plugs because they are higher quality construction and will offer less resistance to whole circuit. So what if you seldom need it's full capacity?...It's there when you do need it, plus it survives longer in shop use compared to bedroom alarm clock use.

Would you enjoy it when you plug in ANYTHING and the cord falls out of the outlet?...Been there, done that.

If you are wiring your shop, not a yuppy garage, but a shop, then use only 12/2 and industrial or hospital grade outlets....If any of your shop tools offer 120/240, then switch them to 240 and wire outlets for them with at least 10AWG.

A SHOP is populated by MEN that use POWER TOOLS and have STIFF electrical with TIGHT recepticals.

If your shop lights dim when you flip something 'on', you need to upgrade or stay in front of the tube.

Just sayin
FluxCore is offline   Reply With Quote
Old 07-24-2012, 05:33 PM   #45
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,755
Default Re: Adding a New Garage Circuit

Basically yes to your questions. To add, NEC requires there to be more than one outlet if using 15A outlets on a 20A circuit. If there is only one outlet then it has to be a 20A. Also if using 15A outlets on a 20A circuit it's best not to daisy chain them using the side connectors, it's best to use pigtails. Actually it's best to use pigtails when connecting outlets, 15A or 20A. IMHO

Quote:
Originally Posted by Ferrino View Post
Why is this the case? Is it because a device that has the 15A 3-pin plug will never draw more than 15A and will therefore never exceed the rated limit of the 15A outlet?

In that case, the only advantage of having a 20A circuit over a 15A circuit is when you have multiple devices running, yes?
pattenp is offline   Reply With Quote
Old 07-24-2012, 06:07 PM   #46
Ferrino
Senior Member
 
Join Date: Mar 2011
Posts: 131
Default Re: Adding a New Garage Circuit

Thanks very much - that's a lot clearer now. I assume a 15A GFCI outlet is OK to use on a 20A circuit too?

Although I don't understand why a single 15A outlet on a 20A circuit is an issue? This is just a curiosity for me, as all of my circuits will have a minimum of 2-3 outlets.

Yes, I would always plan to join wires within a wiring plug instead of at the side-connector screw.
Ferrino is offline   Reply With Quote
Old 07-24-2012, 07:28 PM   #47
Alchymist
Senior Member
 
Alchymist's Avatar
 
Join Date: Mar 2009
Location: Central PA
Posts: 2,441
Default Re: Adding a New Garage Circuit

Quote:
Originally Posted by pattenp View Post
Basically yes to your questions. To add, NEC requires there to be more than one outlet if using 15A outlets on a 20A circuit. If there is only one outlet then it has to be a 20A. Also if using 15A outlets on a 20A circuit it's best not to daisy chain them using the side connectors, it's best to use pigtails. Actually it's best to use pigtails when connecting outlets, 15A or 20A. IMHO
I may be remembering wrong, and I'm sure someone will correct me if I am, but, as I recall the 15 amp DUPLEX outlet is considered two outlets for that purpose. The restriction is on the "15 amp single" outlet.
Attached Images
File Type: jpg 15-Amp Duplex.jpg (13.9 KB, 1 views)
File Type: jpg 15ampsingle.jpg (33.9 KB, 1 views)
Alchymist is offline   Reply With Quote
Old 07-24-2012, 10:21 PM   #48
pattenp
Senior Member
 
pattenp's Avatar
 
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,755
Default Re: Adding a New Garage Circuit

My understanding is the same as yours. I did mean a single outlet not a duplex. Good you gave that clarification.

Quote:
Originally Posted by Alchymist View Post
I may be remembering wrong, and I'm sure someone will correct me if I am, but, as I recall the 15 amp DUPLEX outlet is considered two outlets for that purpose. The restriction is on the "15 amp single" outlet.
pattenp is offline   Reply With Quote
Old 07-24-2012, 10:39 PM   #49
Dick in Wisconsin
Senior Member
 
Dick in Wisconsin's Avatar
 
Join Date: Mar 2012
Location: Grafton, Wisconsin
Posts: 758
Default Re: Adding a New Garage Circuit

Quote:
Originally Posted by FluxCore View Post
Gooberheads, we select 20A outlets and plugs because they are higher quality construction and will offer less resistance to whole circuit. So what if you seldom need it's full capacity?...It's there when you do need it, plus it survives longer in shop use compared to bedroom alarm clock use.

Would you enjoy it when you plug in ANYTHING and the cord falls out of the outlet?...Been there, done that.

If you are wiring your shop, not a yuppy garage, but a shop, then use only 12/2 and industrial or hospital grade outlets....If any of your shop tools offer 120/240, then switch them to 240 and wire outlets for them with at least 10AWG.

A SHOP is populated by MEN that use POWER TOOLS and have STIFF electrical with TIGHT recepticals.

If your shop lights dim when you flip something 'on', you need to upgrade or stay in front of the tube.

Just sayin
This is really good advice.

With the amount of wire you're running and few number of outlets and breakers, wire everything for 20amp and don't worry about it. The suggestion to run 12/3 wire to the workbench and have one circuit for tools and one circuit (separate breakers) for lights is a good one. Pop the tool breaker, and you still have lights, the radio should work, and the digital clock won't reset.

When you wire the outlets, put two duplex outlets in double gang or triple gang boxes; that way you'll reduce the need for power strips. If you use triple, put the outlets at the ends so you have room for more than one wall wart transformer for your cordless stuff and your phone. Put the light switch in the middle if appropriate, or leave it blank.

Wiring 15amp outlets is only nickle and diming yourself to death. Remember what the guy above said about buying quality, heavy duty outlets. You pay for what you get. You're not going to be plugging in a bunch of lamps with 13w CFL bulbs. Your tools will run better on the 20amp circuits too versus being on the "edge" of the circuit every they lug down in heavy going like an oak 6x6 or drilling a 1" hole in thick steel.
__________________
20x22 attached garage (Sears opener w/40w lite, one 75w ceiling lite on pull chain, no heat no running water no TV no AC, one GFCI outlet on main bath circuit in a lousy location), added 8 outlet (4 in each location w/GFCI), 10x20 detached garage (one outlet in wrong location & 75w ceiling light on pull chain), looking to build bigger garage.
#90 Heilig-Meyers Ford Taurus-1996 Suburban 1500-24' enclosed trailer-lots of tools
Wears sound warnings like a badge of honor

Last edited by Dick in Wisconsin; 07-24-2012 at 10:42 PM.
Dick in Wisconsin is offline   Reply With Quote
Old 07-26-2012, 02:36 PM   #50
Ferrino
Senior Member
 
Join Date: Mar 2011
Posts: 131
Default Re: Adding a New Garage Circuit

I thought I read somewhere that outlets must be placed at a minimum distance above concrete floors in a garage?

Quote:
Originally Posted by acer66 View Post
I do not think there are any real rules about the placement of receptacles besides some, I think, when it come to access for disabled people but I don`t think this applies to you.

In general a lot of people will mount the upper receptacles higher than 48" to be able to lean sheet good against the wall and still be able to access the receptacle/switch.

At your workbench I would just mount them where they are the most convenient for you.

It does not matter how far away the old work boxes are placed away from the studs assuming the framing is done somewhat right and you do not have 1/4" drywall on the walls.

If you do not know what is going on in your walls, existing ducting, cables, water lines, etc.
be careful when you start cutting the holes.

You might also have a fire stop right where you want to place your box.
Ferrino is offline   Reply With Quote
Old 07-26-2012, 05:35 PM   #51
acer66
Senior Member
 
acer66's Avatar
 
Join Date: Dec 2010
Posts: 404
Default Re: Adding a New Garage Circuit

I think there is one regarding garage outlets needing to be 18" off the floor due to the sparks igniting vapors but I think that only applies to commercial structures.
acer66 is offline   Reply With Quote