Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Member
Join Date: Aug 2012
Posts: 56
|
Hi all. I've been doing a lot of research and tried to answer this question myself but can't seem to get a clear answer.
First, I live in Portland, OR have a detached garage and a new 200 amp panel in the house. Feeder wiring will run in interior wall about 5', through the crawl space about 35', underground about 5', and then up the garage wall about 5'. It seems I can run 2-2-2-4 service wire by itself in the walls and crawl space, but I am not allowed to run that in conduit in the ground, nor direct bury it (according to an electrician I talked to). A suggestion was made to run the 2-2-2-4 to the end of the crawl space and then using a jbox and split bolts, splice individual conductors and run them underground in PVC conduit. The other option suggested is run PVC conduit from panel to panel and run individual conductors the whole way. Is there an option that I'm missing? I'd rather not do the splicing, and it seems odd that there wouldn't be a bundled option that allows me to run underground a few feet. Many thanks in advance. Justin |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Dec 2011
Location: Plattsburgh, NY
Posts: 327
|
Correct... you cannot run SER in conduit. You need individual THWN wires; or the easier option is mobile home feeder. It is much easier to run SER to a box, transition to conduit, and then run conduit right into the subpanel.
|
|
|
|
|
|
#3 |
|
Member
Join Date: Aug 2012
Posts: 56
|
Ok. That's good to know. It just seems odd that there isn't one type of wire that fits this very common scenario. Considering 3 #2 and 1 #4, and using split bolt connectors wrapped in what looks like a ton of tape, what size j box would you recommend? Can I use a non metal box to avoid having to ground it?
Thanks! |
|
|
|
|
|
#4 | |
|
Senior Member
Join Date: Jul 2012
Location: MD
Posts: 130
|
Quote:
![]() Purchase them at any electrical supply house, sized for your wire. Split bolts require rubber splicing tape, then 3M #33. There is a proper way tape them, and many improper ways. Use a PVC box w/ gasketed cover, say 8x8x4... Personally, I would run conduit the entire way and use THWN conductors. Last edited by '04 Cummins; 08-06-2012 at 03:42 PM. |
|
|
|
|
|
|
#5 |
|
Member
Join Date: Aug 2012
Posts: 56
|
Those look way easier. What are they called?
I'll be pricing out conduit and individual conductors vs. spliced system. Thanks |
|
|
|
|
|
#6 |
|
Senior Member
Join Date: Jul 2012
Location: MD
Posts: 130
|
NSI Polaris lugs. You would want part number IT-1/0.
Here's a Fleabay link for further details: http://www.ebay.com/itm/NSI-Polaris-...item19d3cbfb5c |
|
|
|
|
|
#7 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,940
|
I did the 2-2-2-4 SER from my main panel to a junction box and transitioned to 2-2-2-4 Mobile Home Feeder (MHF) which I ran in 2" PVC conduit to the panel in the detached garage. It is perfectly fine to do a splice. I used splice/reducers and used shrink tube to insulate. The Polaris connectors are very expensive.
|
|
|
|
|
|
#8 |
|
Senior Member
Join Date: Jul 2012
Location: MD
Posts: 130
|
A quick look at prices puts the polaris lugs a bit more, but not by much when you factor in tape or heat shrink... Plus they're so damn easy. When I'm in a crawl space, I want easy, but that's just me
|
|
|
|
|
|
#9 | |
|
Senior Member
Join Date: Sep 2008
Location: Michigan
Posts: 434
|
Quote:
If you can run conduit the whole way from panel to panel that's great, just remember no more then 360 degrees of bend before a pull point. |
|
|
|
|
|
|
#10 |
|
Member
Join Date: Aug 2012
Posts: 56
|
Yep I'm going to line out the pricing. For what it's worth, I'll report back what I find.
I wonder what you all have found easier. Running conduit in a crawl space and pulling through vs. running SER and a junction. I've never run conduit before. It seems straight forward, but could you explain a "pull point"? Thanks |
|
|
|
|
|
#11 |
|
Member
Join Date: Aug 2012
Posts: 56
|
It came out about $25 cheaper to run conduit all the way. At this point my question is about installation. I have post and beam construction with a crawl space, no rim joist so I don't think I have enough room for one of those long sweep 90s to get into the crawl. I plan to use 2" conduit. Is there an offset or some other kind of method to navigate the sill plate?
Thanks |
|
|
|
|
|
#12 |
|
Senior Member
Join Date: Dec 2011
Location: Plattsburgh, NY
Posts: 327
|
If a 90 bend won't fit then put a LB fitting. They're huge, but it'll allow you to make a sharp turn.
|
|
|
|
|
|
#13 |
|
Senior Member
Join Date: Jun 2008
Location: Virginia - USA
Posts: 3,940
|
These are conduit bodies such as LB's, LL's etc. and are used as pull points.
|
|
|
|
|
|
#14 | |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,456
|
Quote:
|
|
|
|
|
|
|
#15 | |
|
Member
Join Date: Aug 2012
Posts: 56
|
Quote:
Thanks! |
|
|
|
|
|
|
#16 | |
|
Senior Member
Join Date: Oct 2010
Location: Oshkosh, WI
Posts: 2,456
|
Quote:
If the wire fits, anything can be done when you have accessible LBs and sweeping corners. The difficulty pulling is directly related to the degress of bends/etc., sharp corners (bad), use of lube, and the diameter of your conduit... as you'd expect. Remember that the professionals use a pull line (NOT push the wire) and like any electrifying activity - use plenty of lube! |
|
|
|
|
|
|
#17 |
|
Member
Join Date: Aug 2012
Posts: 56
|
What kind of lube is best?
|
|
|
|
|
|
#18 |
|
Senior Member
Join Date: Dec 2011
Location: Plattsburgh, NY
Posts: 327
|
|
|
|
|
|
|
#19 |
|
Junior Member
Join Date: Dec 2006
Posts: 6
|
I just finished a jacuzzi install and i 2nd the use of polaris plugs, So simple and such a cleaner job for me anyway. I paid 16 dollars each at California Electric in El Cajon CA.
Rex |
|
|
|
|
|
#20 |
|
Member
Join Date: Aug 2012
Posts: 56
|
OK, I'm ready to run my wire. I decided to use the SER wire instead of conduit. Here is my plan.
Run 2-2-2-4 from inside 200 amp panel down wall and through crawl space. Junction using Polaris plugs (or similar) and put in junction box Transition to 1 1/2" PVC conduit Run 1 1/2" PVC conduit the 4 feet from house to garage at 24" below ground level Use LB fitting to get inside garage This is where I'm confused. Since I'm running individual wires from the junction box in the crawl space, do I have to have conduit all the way to the panel in the garage? I'm assuming so. So how do I get conduit through the wall without it being ugly? Install 100 amp breaker in 200 amp panel in house. Any advice on the plan would be appreciated. Thanks! |
|
|
|
![]() |