Well, after over 1.5 years of Craigslist searching, 20+ calls to people with compressors for sale, and not a single hit (either too late, or the compressor sucked), I gave up and took the high road: I bought a new Campbell Hausfeld XP5810 compressor from my local Lowes. $599 for this: http://www.chpower.com/webapp/wcs/stores/servlet/chPrd3_10051_10001_110213_-1_10646_10689_

Not too bad, I'd say. Now comes the fun part: Wiring it in. I know the motor draws 22A@240v when it runs. I know I needed a minimum of AWG8 wire and a 40A breaker to handle the load, but I found a 30' piece of NM-6/3 w/ ground in the cull pile, and scored that for $40. I'm going to put in a 60A breaker and wire it with this massive cable. I'm also planning on getting a 250A welder soon, so I'll need the 60A breaker soon enough.

SO. Here comes the question part:
1. There isn't a switch on the compressor. I assume thats because I need to run a separate disconnect switch for it, located at the compressor location. Is this correct, and what switch can I use?
2. Any hints on wiring it up? I haven't looked at the wiring diagram yet, but I imagine its pretty easy. Hot1 and Hot2 to two lugs, neutral to another, ground to the box.
3. Any hints for setting things up that you folks with more experience have found? :beer:
 
To avoid these ads, REGISTER NOW!

Stuart in MN

Well-known member
Joined
Sep 8, 2005
Messages
23,114
Location
Minneapolis
Is the compressor going to be within sight of the breaker panel? If so, no local disconnect is needed. If it's not, yes you need a local disconnect. Most any big box store should have a 60 amp 240vac non-fused disconnect for sale, you can probably get one marketed as an air conditioner disconnect pretty cheaply.

The compressor should only need the two hots and a ground for 240vac. The neutral isn't necessary unless for some reason it has a need for 120vac power as well. If that's the case you won't need the white neutral wire.
 
OP
S

sharkytm

ALLIANCE MEMBER
Joined
May 17, 2008
Messages
596
Location
Pocasset, MA
Without a local disconnect, I won't have a way to turn it on or off... There was no switch supplied. I'm not sure if my welder needs the neutral, so I bought the 3+g to be safe.
 

rinny_tin_tin

Well-known member
Joined
Dec 20, 2008
Messages
636
Location
Northern Virginia
Well, after over 1.5 years of Craigslist searching, 20+ calls to people with compressors for sale, and not a single hit (either too late, or the compressor sucked), I gave up and took the high road: I bought a new Campbell Hausfeld XP5810 compressor from my local Lowes. $599 for this: http://www.chpower.com/webapp/wcs/stores/servlet/chPrd3_10051_10001_110213_-1_10646_10689_

Not too bad, I'd say. Now comes the fun part: Wiring it in. I know the motor draws 22A@240v when it runs. I know I needed a minimum of AWG8 wire and a 40A breaker to handle the load, but I found a 30' piece of NM-6/3 w/ ground in the cull pile, and scored that for $40. I'm going to put in a 60A breaker and wire it with this massive cable. I'm also planning on getting a 250A welder soon, so I'll need the 60A breaker soon enough.

SO. Here comes the question part:
1. There isn't a switch on the compressor. I assume thats because I need to run a separate disconnect switch for it, located at the compressor location. Is this correct, and what switch can I use?
2. Any hints on wiring it up? I haven't looked at the wiring diagram yet, but I imagine its pretty easy. Hot1 and Hot2 to two lugs, neutral to another, ground to the box.
3. Any hints for setting things up that you folks with more experience have found? :beer:

Stuart nailed it - you can use your 60 A breaker to shut off power to the comp if the compressor is within sight of the breaker. Otherwise, get one of those AC disconnect switch box. Since you already have the neutral - run it and leave it disconnected on both ends - You may need it later on

Enjoy yer new cmp
 
OP
S

sharkytm

ALLIANCE MEMBER
Joined
May 17, 2008
Messages
596
Location
Pocasset, MA
14cfm doesn't seem to be alot for a big compressor...what are your plans for it?

Its the best I could find for under a grand. Ingersoll Rand makes the 2340N5, same specs (5HP, 80G, 15CFM), but its a lot more expensive.

I actually don't have a huge amount of air tools yet, but I can't stand my old 33G 1.5hp oil-less Craftsman, too loud, and not enough air to use for much. I do some sandblasting, so I definitely needed something bigger.
 

sonett43

Well-known member
Joined
May 31, 2008
Messages
58
I bought the same compressor, and a 220v disconnect from lowes for under $20 for the disconnect. Ran the electric last week, doing the black pipe and hose reels in the next week or 2.
 

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
If it was my compressor, I'd put in a 60A breaker panel so supply the garage. Then put in a 30A? breaker in the panel. For 5hp compressor drawing 22amps, you shouldn't need a 40A breaker. You can use your #8 wire from the breaker panel to the 30A breaker. Oversizing the wire never hurts. This way, you use the built in switch on the compressor to cycle the compressor when it is in use, and when not in use, you can turn off the 30A breaker so it doesn't try to run.
I'm running my 5hp compressor on a 30Amp breaker and #8 wire from my 100A panel. The oversize wire allows easy starts even in very cold weather so the motor doesn't eat itself up.
Even my little 110v compressor which needs a 20A breaker and #12 wire is running on its 20A breaker and #10 wire. It used to drop the 20A breaker in cold weather trying to start on #12 wire, but with #10 wire, that doesn't happen.
 
OP
S

sharkytm

ALLIANCE MEMBER
Joined
May 17, 2008
Messages
596
Location
Pocasset, MA
If it was my compressor, I'd put in a 60A breaker panel so supply the garage. Then put in a 30A? breaker in the panel. For 5hp compressor drawing 22amps, you shouldn't need a 40A breaker. You can use your #8 wire from the breaker panel to the 30A breaker. Oversizing the wire never hurts. This way, you use the built in switch on the compressor to cycle the compressor when it is in use, and when not in use, you can turn off the 30A breaker so it doesn't try to run.
I'm running my 5hp compressor on a 30Amp breaker and #8 wire from my 100A panel. The oversize wire allows easy starts even in very cold weather so the motor doesn't eat itself up.
Even my little 110v compressor which needs a 20A breaker and #12 wire is running on its 20A breaker and #10 wire. It used to drop the 20A breaker in cold weather trying to start on #12 wire, but with #10 wire, that doesn't happen.

It needs a 35A breaker to run. There is NO switch on the compressor, other than the pressure switch, I don't know if that was what you were referring to?

I'm going to put in a disconnect, I don't like using a breaker as a switch. The garage already has a 100A subpanel, and another 60A sub for the upstairs apartment (with its own meter). I'd like to avoid another subpanel.

Thanks for the info.

Sonett: Do you have any pictures of your setup? Where did you get your regulator and filter? I'm having trouble finding an affordable reg that can handle 175psi.
 

sonett43

Well-known member
Joined
May 31, 2008
Messages
58
no photos yet, but I can snap some tomorrow.

I found a 160 PSI regulator with 1/2" inlet and outlet on ebay, that will do the job for me.

I need to travel out of town this week, so progress will likely occur next week.

Lewis
 
To avoid these ads, REGISTER NOW!

Aceman

Well-known member
Joined
Jan 28, 2007
Messages
2,513
Location
Eastern Oregon
I don't get what the deal is with folks wanting to lump all their equipment onto one 240 circuit?

You might have 20 dollars in wire and an 8 dollar breaker. Is $28 just too much to spend for a dedicated circuit to an air compressor?
 

ironroad 9c1

Banned
Joined
Sep 3, 2005
Messages
758
Location
Gum spring,VA
funny you mentioned your craftsman 33 gal..lol I have the same thing for a backup, bought it maybe 7 years ago, and wore out the piston ring useing it, 12 bucks later for a new ring and I was back in business. decent unit, but not for anything that requires alotta air.
 
OP
S

sharkytm

ALLIANCE MEMBER
Joined
May 17, 2008
Messages
596
Location
Pocasset, MA
I don't get what the deal is with folks wanting to lump all their equipment onto one 240 circuit?

You might have 20 dollars in wire and an 8 dollar breaker. Is $28 just too much to spend for a dedicated circuit to an air compressor?

Try $65 in wire, $30 for a breaker, and another 1" hole through all my studs.
Plus, I'll never be using the compressor and welder simultaneously. I've got 2 other 240v circuits in the garage, just not any other 60A devices.

I've been looking at larger AC's and how come in the technical specifications they never list a breaker amperage requirement?
They usually just list the amps needed running and at startup. Its up to you to figure out what 20% overhead is, and calculate the breaker size. Basically, industrial compressors assume that you have the power and enough intelligence to run the correct size wire/breaker. I guess thats the price we pay for industrial equip.
 

Charles (in GA)

Well-known member
Joined
Jan 11, 2006
Messages
12,489
Location
50 mi south of Atlanta
Try $65 in wire, $30 for a breaker, and another 1" hole through all my studs.
Plus, I'll never be using the compressor and welder simultaneously. I've got 2 other 240v circuits in the garage, just not any other 60A devices.

What kind of panel do you have that requires a $30 double pole breaker???

Square D QO series double pole breakers are about $15 up thru 60 amp, everyone else (Seimens, GE, Homeline) are about $10 or less. When you get to 100 amp double pole, you finally get to about $35 for them, $50 for Square D.

Charles
 

35mastr

Well-known member
Joined
Dec 6, 2007
Messages
2,534
Location
Norcal
I have an old panel.They require the Zinsco breakers.Every time I get a 30 or bigger its 85.00 at Dales.They are the only ones that carry them around here.
 

nadogail

Well-known member
Joined
Jan 23, 2009
Messages
31,959
Location
Coronado, CA
What you have is a F...king Zinsco, they have earned a bad reputation for not opening. I am not the most experienced electrician around, but I pay attention to what the more experienced journeymen have to say. As a rule, Zinsco Breakers are referred to as Fu..ing Zinscos.

I respectfully suggest you plan on changing out the panel to a modern one.

Perhaps you might consider a sub panel to control the circuits in your garage, then when the time and resources seem right replace the panel holding those Antique Zinsco breakers.
 

35mastr

Well-known member
Joined
Dec 6, 2007
Messages
2,534
Location
Norcal
What you have is a F...king Zinsco, they have earned a bad reputation for not opening. I am not the most experienced electrician around, but I pay attention to what the more experienced journeymen have to say. As a rule, Zinsco Breakers are referred to as Fu..ing Zinscos.

I respectfully suggest you plan on changing out the panel to a modern one.

Perhaps you might consider a sub panel to control the circuits in your garage, then when the time and resources seem right replace the panel holding those Antique Zinsco breakers.

Ya,I know what your saying.I have a sub in the garage.Its probably as old as that one too.

When I upgrade the panel to 200 Amps I am going to change both of them.

I have a hundred now.While on the subject.What would it cost to, bring in 200 Amps?
 

mdoolittle

Well-known member
Joined
Jun 18, 2008
Messages
272
Location
IOWA

Gary S

Well-known member
Joined
Dec 27, 2008
Messages
2,972
Location
Bismarck, ND
Both my compressors have a two position switch on them. They can be in "Auto" or "Off".
I always leave them Off when not using them, and in Auto when using them. Auto allows them to run as needed as air dictates. Off prevents them from running at all.
I suspect that most compressors have similar switches so you don't need to be turning the breaker off.

And, I see no need to fuse a 22 or 23 amp compressor at 40 amps. As sharkytm mentioned above, you want at least 20% overhead. Doing simple math, 20% more than 22-23 amps is 26.4-27.6 amps, still below a 30amp breaker. Mine cycles happily all day on a 30 amp breaker. Using oversized breakers just makes things burn up faster and hotter if something goes wrong. I want my breakers to trip if anything ever goes wrong in the motors, and trip as fast as possible to prevent more damage.
 