Welcome to the The Garage Journal Board forums. You are currently viewing our boards as a guest which gives you limited access to view most discussions and access our other features. By joining our free community you will have access to post topics, communicate privately with other members (PM), respond to polls, upload content and access many other special features. Registration is fast, simple and absolutely free so please, join our community today! If you have any problems with the registration process or your account login, please contact contact us. |
|
|||||||
![]() |
|
Thread Tools | Display Modes |
|
|
#1 |
|
Junior Member
Join Date: Mar 2009
Posts: 16
|
I have a 3 phase 1750 rpm motor on my compressor.
I would like to replace it with a single phase motor. Can I just replace and all will be ok? |
|
|
|
|
|
#2 |
|
Senior Member
Join Date: Apr 2008
Location: Cedar,BC
Posts: 1,029
|
Sort of.Your new single phase motor will draw almost double the current for the same hp,the control and wiring will likely need to be upsized as well.Post some more info,I'm sure this has been done in the past by some of the other members.
|
|
|
|
|
|
#3 |
|
Senior Member
Join Date: Oct 2008
Location: Dixion, Missouri
Posts: 360
|
Yes and no. It doesn't always go without a hitch. A three phase motor has great start up torque. normally greater then that of even a single phase with the start and run caps. So a three phase compressor while having a cyl head relief and so on does not always require systems to function for the compressor to be operational. So if the pressure and or flywheel weights (or any other start up aid) reliefs are not working correctly, the single phase motor would not be able to start the compressor even though it seemed to be functioning fine with a three phase motor. How may horsepower is the three phase motor. I would recommend going with a slightly high horsepower if going single phase. I am only basing this on my own experiences and others may disagree but I feel in general 3 phase motors are more commonly rated with stronger service factors. So a HP rating of a single phase motor may be actually less then the comparable HP motor of the three phase.
__________________
Matt G |
|
|
|
|
|
#4 |
|
Senior Member
Join Date: Dec 2008
Posts: 3,742
|
what about getting a VFD and keeping the 3ph motor? They have really come down in price over the last couple years.
|
|
|
|
|
|
#5 |
|
Senior Member
Join Date: Dec 2007
Location: visalia ca
Posts: 8,474
|
go to ebay and get a bargain priced VFD to run the thing
bob
__________________
my wife says that I have never met a tool I havent liked. people on the other hand...... |
|
|
|
|
|
#6 |
|
Senior Member
Join Date: Aug 2005
Location: On the Right Coast
Posts: 1,356
|
Another vote for a VFD.
All responses so far are great. Scott
__________________
Haul your MX bike without straps - visit www.mxtras.com to see how Custom Storage Cabinets with FREE plans - http://www.garagejournal.com/forum/s...ead.php?t=1773 Link to workstation plans for download (FREE) - http://reference.toolandfab.com/writ...nets/index.htm |
|
|
|
|
|
#7 | |
|
Senior Member
Join Date: Dec 2008
Location: Northern Virginia
Posts: 636
|
Quote:
However, your inrush current (5 X cont. running current) would also be about 73% higher - or 100 A vice 60A - so be prepared for 8 % or greater voltage dip - dimming lights etc. |
|
|
|
|
|
|
#8 |
|
Senior Member
Join Date: Feb 2009
Location: York, PA
Posts: 731
|
the variable frequency drives can be hard on the 3-ph motors. It's not a true 3-ph. I've got a 3-ph vertical mill and I'm currently looking for a rotary phase converter. They are much better for creating 3-ph from single phase.
Another option-- buy a panel from ebay that allows you to "create" a rotary phase converter. you could source your own 3-ph motor and have real three phase. |
|
|
|
|
|
#9 |
|
Senior Member
Join Date: Nov 2008
Location: Maine
Posts: 3,655
|
How old is the 3 phase motor?, If very old I'd up the HP on a new single phase
|
|
|
|
|
|
#10 | |
|
Senior Member
Join Date: Dec 2008
Posts: 3,742
|
Quote:
how is that? they provide a softstart function limiting startup current and stress on the motor. How are they not true 3ph? They use a 3ph inverter to create the output to the motor. (note: I have not looked at the waveform of the output of one on a scope) |
|
|
|
|
|
|
#11 |
|
Senior Member
Join Date: Aug 2008
Posts: 267
|
a lot of it depends on what size the motor is my works new location they moved to 5 years ago can only get single phaze in there 400amp service and we are maxing it out. 10hp single phase will run 60amps and we have a 5hp runs 30 and fan anouther 30 and every time the compressor starts up you see the lights flicker due to the big draws on it. loking back on it we are wishing we with with a phase converter. Curently have 4 3phase motors sitting there been thinking of getting one big one so i can make a converter to run them
|
|
|
|
|
|
#12 | |
|
Senior Member
Join Date: Jun 2006
Location: Eastern Iowa
Posts: 4,251
|
Quote:
I've looked at the 3 phase coming off my Boston Fincor VFD(driven with single phase), and it looks a hell of alot better than most "real" 3 phase. Unless you spend big bucks on a rotary convertor most of them are a far cry from "real" 3 phase too. As far as being "hard" on 3 phase motors, if that's the case there's alot of 3 phase motors out there that are about to smoke. Look around the typical factory these days, except for fan motors and other basic operations, 3 phase motors in most automated machines are running very happily off of VFD's. Open the control cabinets and you'll find a host of VFDs right along side the PLCs, or integrated into the PLCs. My vote is for the VFD..... |
|
|
|
|
![]() |